Hi, I replaced the previous Vaisala Barro sensor with CS106
but use the same program. ( its offset value was set as 600).
I am getting readings that are 30mb higher than the standard
value. I am using it at 6-8 Mtrs higher than sea level).
Can someone tell me whether to set the offset value at 500, as the present range of CS106 is 500-1100mb or any other way to fix the problem.
Thanks.
Not sure what your previous sensor was but many were scaled 600-1100 mB for 2.5 V output. The CS106 outputs 2.5V for 500-1100 mB so you need to change the offset to 500 and the multiplier to 0.24 (it was probably 0.20 before).