Configuration of installation : Acquisition of vibrating wire with CR1000 and four multiplexer in series via a CV module. This configuration worked fine until yesterday. Today, the datalogger "CR1000" no longer data acquisition. (No change in the program)
Tests conducted :
The multiplexers are reading them (click relays)
Measurement upstream of the module "CV" frequency ok
Measure downstream module "CV" frequency ok
Measure on the way to the datalogger: frequency ok
Cable in good condition
We will test the track with a potentiometric sensor tomorrow, do you know of other tests to be done to control the installation?
Check the Status table in the CR1000 for any errors.