We have a dozen new Ott Pluvio II's and have installed 3 using 1K loggers with no problem using the slow sequence function so the rest of the program doesn't delay while the results are returned. (lots of things go on at the top of the hour). I am going to install one(pluvio II) at an existing site that has a 10X-TD with a busy program. With the standard 10x OS, I could have another table with a different scan rate and it'd be fine (I only need the data at the top of the hour when everything else is summating). Before I just add the SDI instr to the middle of the existing prog, and risk the delays, is there a better way,..ie sub routine,....I have lost any skill I did have with edlog once the K's came out. Any help would be much appreciated.
Mike
Mike, I know this is an old post and hopefully you've found your solution. Maybe aC! would be the best command for your application. We commonly use it with probes that take a long time to measure and respond.