Bobfbks Feb 23, 2010 01:09 AM

Hi,
I was wondering (and not really seeing in the CR1000 literature) the max current load the 12V Power Out terminals can support. Is the value the same as for switched 12 volts? thanks


IslandMan Feb 23, 2010 11:34 AM

Bob,

Page 4-2, Table 4.1-1 of the CR1000 Manual:
12V + SW12: <3.0A @20C
I'm assuming you could take the .9A from the SW12 @20C and subtract it from the 3 and arrive at 2.1A for the 12V terminals @ 20C.

http://www.campbellsci.com/documents/manuals/cr1000.pdf

IslandMan


Bobfbks Feb 23, 2010 07:03 PM

Cool, thanks very much. That's exactly what I was looking for.