khkim Feb 17, 2010 01:01 AM

Hi,

I have a Vaisala WXT520. In order to connect with CR10X, I am trying to program using Edlog 32 in LoggerNET with reference a manual, 'http://www.campbellsci.com/documents/manuals/wxt520.pdf'

But, I could not connect WXT520 with CR10X. Would you please check my CSI code.

Thanks for your support.

The following code is the CR10X program.

;{CR10X}
;
*Table 1 Program
01: 1.0000 Execution Interval (seconds)

1: Batt Voltage (P10)
1: 1 Loc [ Batt_Volt ]

2: If time is (P92)
1: 0 Minutes (Seconds --) into a
2: 1440 Interval (same units as above)
3: 30 Then Do

3: Signature (P19)
1: 2 Loc [ Prog_Sig ]

4: End (P95)

5: SDI-12 Recorder (P105)
1: 0 SDI-12 Address
2: 1 Start Measurement (aM1!)
3: 2 Port
4: 3 Loc [ Value1 ]
5: 1.0 Multiplier
6: 0.0 Offset

6: Excitation with Delay (P22)
1: 1 Ex Channel
2: 0 Delay W/Ex (0.01 sec units)
3: 50 Delay After Ex (0.01 sec units)
4: 0 mV Excitation

7: SDI-12 Recorder (P105)
1: 0 SDI-12 Address
2: 2 Start Measurement (aM2!)
3: 2 Port
4: 9 Loc [ Value7 ]
5: 1.0 Multiplier
6: 0.0 Offset

8: Excitation with Delay (P22)
1: 1 Ex Channel
2: 0 Delay W/Ex (0.01 sec units)
3: 50 Delay After Ex (0.01 sec units)
4: 0 mV Excitation

9: SDI-12 Recorder (P105)
1: 0 SDI-12 Address
2: 3 Start Measurement (aM3!)
3: 2 Port
4: 12 Loc [ Value10 ]
5: 1.0 Multiplier
6: 0.0 Offset

10: If time is (P92)
1: 0 Minutes (Seconds --) into a
2: 10 Interval (same units as above)
3: 10 Set Output Flag High (Flag 0)

11: Set Active Storage Area (P80)
1: 1 Final Storage Area 1
2: 101 Array ID

12: Real Time (P77)
1: 1220 Year,Day,Hour/Minute (midnight = 2400)

13: Average (P71)
1: 1 Reps
2: 9 Loc [ Value7 ]

*Table 2 Program
02: 0.0000 Execution Interval (seconds)

*Table 3 Subroutines

End Program

-Input Locations-
1 Batt_Volt 1 0 1
2 Prog_Sig 1 0 1
3 Value1 1 0 1
4 Value2 1 0 0
5 Value3 0 0 0
6 Value4 0 0 0
7 Value5 1 0 0
8 Value6 0 0 0
9 Value7 1 1 1
10 Value8 0 0 0
11 Value9 0 0 0
12 Value10 1 0 1
13 Value11 0 0 0
14 Value12 0 0 0
15 Value13 0 0 0
16 Value14 0 0 0
17 Value15 0 0 0
18 _________ 0 0 0
19 _________ 0 0 0
20 _________ 0 0 0
21 _________ 0 0 0
22 _________ 0 0 0
23 _________ 0 0 0
24 _________ 0 0 0
25 _________ 0 0 0
26 _________ 0 0 0
27 _________ 0 0 0
28 _________ 0 0 0
-Program Security-
0000
0000
0000
-Mode 4-
-Final Storage Area 2-
0
-CR10X ID-
0
-CR10X Power Up-
3
-CR10X Compile Setting-
3
-CR10X RS-232 Setting-
-1
-DLD File Labels-
0
-Final Storage Labels-
0,101,25478
1,Year_RTM,14143
1,Day_RTM
1,Hour_Minute_RTM
2,Value7_AVG~9,11381

* Last updated by: khkim on 2/16/2010 @ 6:04 PM *


jra Feb 19, 2010 07:32 PM

I suspect it is a configuration or timing problem. One easy thing to try is slowing down your execution interval to 15 seconds.

How do you have the WXT520 configured? Check its address, that it is SDI enabled and what the update intervals are.

Check wiring. Is the brown wire in 12V and not SW 12V?

Let us know what you find.