Hi, i'm a new user of this forum and i'm not expert in datalogger programming. Can you give me some instruction for to connect 16 probes of soil water content (10hs) to Cr1000?
Grazie
Connect all the white wires to the 12 volt switched power supply; red wires to the SE channels and the bare wires to the nearest ground.
The program wil measure and store the mV outout from the sensors every 15 minutes
Public mV(16)
DataTable (SWC,True,-1)
Sample (12,mV(),FP2)
EndTable
BeginProg
Scan (15,min,0,0)
SW12 (1 )
Delay (0,10,mSec)
VoltSe (mV(),16,mV2500,1,1,0,250,1.0,0)
SW12 (0 )
CallTable SWC
NextScan
EndProg