Hi,
I have a CR1000X.
Is it possible to save the TIMESTAMP in a datatable with 1 days in mins than the real time?
It is for a weather program with daily data.
My weather standard requires the measurement of the maximum daily temperature from 6am to 6am. The data corresponds to the previous day.
Example :
The Real time is 2024-10-23 6:00:00
DataTable (MTO,True,-1)
DataInterval (6,24,Hr,0)
Maximum (1,Temp,FP2,False,False)
EndTable
Begin prog
Scan(60,min,100)
MEASURE....
Calltable MTO
Nextscan
Endprog
The table OUT TIMESTAMP is 2024-10-23 6:00:00
But, i want to write the TIMESTAMP to 2024-10-22 6:00:00
Thank you for your help
You cannot override the TimeStamp column. You could create another column in the data table for the adjusted time.
To calculate the adjusted timestamp, use the SecsSince1990 on Public.TimeStamp and subtract an offset.
Public AdjustedTime(2) As Long DataTable (Test,True,-1 ) DataInterval (1,10,Sec,10) Sample (1,AdjustedTime(1),Nsec) EndTable 'Main Program BeginProg Scan (1,Sec,0,0) AdjustedTime(1) = SecsSince1990 (Public.TimeStamp(1,1),1) - 86400 'AdjustedTime(2) = 0 'Nanoseconds are left zero CallTable Test NextScan EndProg