CR1000 connet PT-100 3 wier


foxly Mar 3, 2012 08:06 AM

Dear all,

I am working on PT-100 3-wire connet CR1000

CR1000→PT-100 3-Wire

Hi→ A

Lo→ no connet

G→ B

G→ B

A.B bridging 1K Ohm.

Connet So correctly ??

Thanks campbell all

* Last updated by: foxly on 3/3/2012 @ 1:52 AM *


Nico Mar 3, 2012 06:16 PM

prob not correct..

You need to send a constant current through the temperature depended resistor (PT100) to measure a voltage drop that will correlate with the temperature.

See CS 3-wire half bridge module that does exactly that:
http://s.campbellsci.com/documents/us/manuals/3whb.pdf

And then read the CR200 manual about bridge measurements on page 41:
https://s.campbellsci.com/documents/us/manuals/cr200.pdf


foxly Mar 5, 2012 01:31 AM

Dear Nico

Thanks you

I will try connet.