I set up a PC (Loggernet) to CR1000 connection via two MD485's following the instructions for a transparent connection as described in the MD485 user manual.
This connection worked fine.
I then replaced the CR1000 with a CR10X and Loggernet could not communicate with the CR10X via the MD485's.
I know that the CR10X works because I can communicate with it via a direct link using a SC-USB.
Any suggestions on what setup changes I need to make in order to communicate with the CR10x (or multiple CR10x's) via a MD485 multi-drop network?
Thanks
The default settings for the MD485 are to use the CS I/O port, addressed as SDC7. If you are using a CR10X, I suggest you try changing the "CS I/O Mode" of the MD485 connected to the CR10X to "Modem Enable"