I am trying to communicate using PC200W 4.1 software with a CR10X. My system components are:
USB output on Dell laptop running Windows XP SP3
to a Belkin UBS/Serial converter (COM6)
to a SC32B interface
to the CR10X
When I run the Communications Test, I get the error:
"The attempt to communicate with CR10X failed, but a PakBus datalogger with a PakBus address of 1 was found."
Has anybody esle encountered this error? It appears to be either an error in my communicaion protocal to the datalogger, or a software error or lock within the CR10X.
I can access the CR10X using a CR10KD key pad and run a temperature test.
Thanks,
Jack Kayser
US Bureau of Reclamation
Instrumentation Group
Try to connect by choosing the cr10x-pb from the list. The 10x appears to have a pakbus operating system. If you want to load an array based OS on the 10x you can pull one down from our website, under the support menu/downloads, Follow the instructions on the load os tab in device configuration utility when you choose the 10x from the list.
The suggestion to choose CR10X-PB from the list worked.
Thanks for you help.