HMP 45 C - power control 5V or 12V?


Nico Oct 11, 2011 05:12 AM

I couldn't find anything in the datasheet for the 'older' HMP45C sensors, which have the orange power control wire.
There is a wiring table at the end of the actual datasheet, but it doesn't tell if these control inputs are ok with 12V DC.

Anyone?


Dizbert Oct 28, 2011 02:53 AM

You can find Campbell's manual for the HMP45C at:

http://www.campbellsci.com/documents/manuals/hmp45c.pdf

The older probes with the orange wire contain their own power (12V red lead) switch in their cable. The orange wire goes to a control port which is set high to turn the sensor on prior to measurement, and then set low following the measurement to turn off power to the sensor.